消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

公共厨房内的配电箱,需要设置成防爆配电箱吗?

公共厨房内的配电箱,需要设置成防爆配电箱吗?

地精修补匠 | 2023-05-31 11:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

安洪全 2023-05-31 13:08 10 [回复]举报

没有硬性要求


民用建筑电气设计标准 GB51348-2019

9.8.6 厨房设备的电气设计应符合下列规定:    

1 厨房设备的配电线路应装设过负荷保护、短路保护及剩余电流动作保护;    

2 厨房设备电源开关除设备上自带的开关外,宜布置在干燥、便于操作的场所,并满足安装场所相应的防护等级要求;    

3 厨房内电缆槽盒、设备电源管线,应避开明火2.0m 以外敷设;    

4 厨房内电缆槽、盒应避开产生蒸汽等热气流2.0m 以外敷设;    

5 厨房设备应设置等电位联结。

地精修补匠   回复: 安洪全2023-06-01 06:57

谢谢

0    0 [回复]举报

安洪全   回复: 地精修补匠2023-06-01 08:52

不客气,还是为魔兽争霸的爱好者,哈哈哈

共同学习,共同进步

0    0 [回复]举报

地精修补匠   回复: 安洪全2023-06-07 15:32

哈哈被发现了

0    0 [回复]举报

nickel 2023-06-01 08:09 10 [回复]举报

应该不需要设置成防爆。

根据GB50058-2014 爆炸危险环境电力装置设计规范:

1 总则

1.0.2 第6条:

本规范不适用于下列环境:

以加味天然气作燃料进行采暖、空调、烹饪、洗衣以及类似的管线系统;

一般的厨房,我们这边设计是不做爆炸危险区域划分相关工作的。

地精修补匠   回复: nickel2023-06-01 08:42

谢谢

0    0 [回复]举报

关闭

关闭

手机APP下载