消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟口设置高度

排烟口应设置在顶棚或者靠近在顶棚的墙面上,但考虑现场施工难度,对于顶棚高度超过3m的建筑物,是否可以将排烟口设置在距地面2.1m的高度以上?是否有相关规范依据支持?

凡人不繁人 | 2023-05-08 21:01
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

周家斌 2023-05-09 09:07 00 [回复]举报

可以,只要在储烟仓内,同时满足db值和排烟量就可以

牛疼 2023-05-09 09:14 00 [回复]举报

具体得看顶棚高度是多少,如果超5米,清晰高度估计无法满足。

消防工作者 2023-05-09 09:52 00 [回复]举报

主要考虑顶棚距离地面的净空高度,设计的储烟厚度,应满足排烟口在储烟层内和最小清晰高度的计算要求。可以参考《建筑防烟排烟系统技术标准》GB51251-2017第4.6.2条和4.6.9条规定要求。

冀消专 2023-05-10 11:18 00 [回复]举报

尽可能设置在高处,高于清晰高度即可,否则计算出排烟口尺寸过大。

GANSTER 2023-05-17 09:43 10 [回复]举报

与设计协商解决

潘天坤 2024-07-03 15:24 00 [回复]举报

空间净高大于3米的场所,如果排烟口装在2.1米的区域,可能存在烟层厚度过小导致单个排烟口最大允许排烟量不符合设计要求

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

关闭

关闭

手机APP下载