防火隔墙厚度有要求吗?

砖墙砌筑的防火隔墙耐火极限两小时,这个砌筑的墙体厚度哪个规范里面有规定,最小厚度是多少毫米?

子不语 | 2024-12-06 09:44
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

缱绻一夏 2024-12-06 10:36 00 [回复]举报

查建筑设计防火规范最后一页的附表

张治福 2024-12-06 10:47 00 [回复]举报

有哦,建筑设计防火规范的附录的内容有哦

附录 各类建筑构件的燃烧性能和耐火极限

李勤 2024-12-06 10:51 00 [回复]举报

看建规后边附录。

消防网友67367 2024-12-06 10:52 10 [回复]举报

附录C 隧道内承重结构体的耐火极限试验升温曲线和相应的判定标准 C.0.1  RABT和HC标准升温曲线应符合现行国家标准《建筑构件耐火试验可供选择和附加的试验程序》GB/T 26784的规定。 C.0.2 耐火极限判定标准应符合下列规定:    1 当采用HC标准升温曲线测试时,耐火极限的判定标准为:受火后,当距离混凝土底表面25mm处钢筋的温度超过250℃,或者混凝土表面的温度超过380℃时,则判定为达到耐火极限。    2 当采用RABT标准升温曲线测试时,耐火极限的判定标准为:受火后,当距离混凝土底表面25mm处钢筋的温度超过300℃,或者混凝土表面的温度超过380℃时,则判定为达到耐火极限。

周家斌 2024-12-06 11:09 00 [回复]举报