消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

采用自然对流排烟的方式,工业建筑执行排烟距离净高的2.8倍的限制吗?


mshm | 2024-06-15 16:01
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

黄-江西省景德镇市 2024-06-15 16:46 00 [回复]举报

“不应”和“应”具有同等效力,应按规范执行。

潘天坤 2024-06-15 21:09 00 [回复]举报

从规范来说,需要遵守,分号之前工业建筑没有是否具备自然对流条的条件说明,所以个人认为是均要执行

最后讨论下2.8倍的要求:空间净高不大于10.7米的场所,按照30米执行;空间净高大于10.7米的场所按照净高的2.8倍执行(10.7*2.8=29.96米)

烟规编制组有个复函,有提到空间净高大于10米的场所,可以按照2.8倍执行,然后考虑到10.7*2.8比较接近30米,不少人认为可以放大到10.7米

建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准
上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

mshm   回复: 潘天坤2024-10-19 17:25

按照图示,反推每侧排烟窗负担排烟距离75/2=37.5米,37.5/2.8=13.39米,净高大于13.39米才能实现。按照复函的说法,大于10米,可不考虑2.8倍。

0    0 [回复]举报

关闭

关闭

手机APP下载