老旧建筑,屋面高位水箱间只设置稳压泵系统,没有消防水泵房,这类系统应该归属于低压系统还是临时高压系统?

HONG MAO | 2024-06-13 09:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

南明离火 2024-06-13 11:33 00 [回复]举报

自来水管直接供进去?

潘天坤 2024-06-13 13:29 10 [回复]举报

根据GB50974消水规术语描述:

低压消防给水系统为能满足车载或手抬移动消防水泵等取水所需的工作压力和流量的供水系统。

高压消防给水系统为能始终保持满足水灭火设施所需的工作压力和流量,火灾时无须消防水泵直接加压的供水系统。

临时高压消防给水系统为平时不能满足水灭火设施所需的工作压力和流量,火灾时能自动启动消防水泵以满足水灭火设施所需的工作压力和流量的供水系统。

一路同行 2024-06-13 13:48 00 [回复]举报

没有消防水泵房,应该是市供水,设稳压泵?

黄-江西省景德镇市 2024-06-13 16:25 10 [回复]举报

高位消防水箱+稳压泵也就是平时保压,稳压泵流量太小,一旦发生火灾,给水流量是达不到要求的,甚至比自重产生的流量还差一大截。如果市政给水压力就能满足该建筑消防用水的要求,那么设高位水箱和稳压泵就没意义了,多余,是不合规的。

同同不同 2024-06-14 09:20 00 [回复]举报

这不糊弄事儿的么