消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

7层防火分区的末端试水开启,但是2-6层的水流指示器均动作,是什么原因呢?

7层防火分区的末端试水开启,但是2-6层的水流指示器均动作,是什么原因呢?

漂移 | 2024-04-07 08:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

一半一半 2024-04-07 16:36 00 [回复]举报

水流波动的可能性大些,调一下水流指示器灵敏度试试

阿龙 2024-04-07 17:05 00 [回复]举报

2-7层应该都是一个报警阀组吧,7层末端开了报警阀阀瓣被冲开,报警阀下腔的带压水过去会形成一点水流波动,正常情况下没什么影响,如果很介意的话可以调节一下2-6层水流指示器的灵敏度。

漂移   回复: 阿龙2024-04-17 08:37

水流指示器可以调灵敏度?怎么调呀?

0    0 [回复]举报

阿龙   回复: 漂移2024-06-21 14:57

水流指示器可以调节松紧来调节灵敏度的,如果太灵敏了可以调紧一点。

0    0 [回复]举报

667248 2024-04-07 17:23 00 [回复]举报

查看一下设计图实际安装。

牛疼 2024-04-08 09:43 00 [回复]举报

1、2-7层的喷淋是同一湿报阀管控的情况下,此类情况属于正常现象。

2、2-7层的喷淋不是同一湿报阀管控的情况下,此情况大概率是湿报阀坏了。

2024-04-10 08:19 00 [回复]举报

这种情况非常少见,有没可能各层的水流指示器安装方向反了?

关闭

关闭

手机APP下载