我看到有的设计图纸中,为什么住宅建筑首层既设置了火灾显示盘,又设置区域报警器?在我的理解里,火灾显示盘和区域报警器没什么不同吧,区域报警器除了报警和显示功能也没有控制功能啊!为啥一个位置设置两个同一种功能的设备呢?还有人说这是哪个规范里要求的,我找了很久没找到哪个规范里的,请问有没有哪位朋友知道是哪个规范里的,烦请告知一下!

好好干 | 2024-01-25 23:21
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

yizhongdayang 2024-01-26 10:45 00 [回复]举报

       根据国家标准《火灾报警控制器》(GB4717-2005),火灾报警控制器按照应用方式分为独立型、区域型、集中型、集中区域型四种类型。区域型火灾报警控制器是具有向其他控制器传递信息功能的控制器,具有火灾报警控制器相应的功能,如火灾报警、故障报警、自检、复位、屏蔽等,并且至少可以启动声光警报器等消防设备。

       火灾显示盘是安装在楼层或报警区域内的火灾报警显示装置。当建筑物内发生火情后,火灾报警控制器发出报警信号,同时把报警信号传输到失火区域的火灾显示盘上。

       综上,火灾显示盘是火灾自动报警系统的末端设备,是用来接收、显示火灾报警控制器发出的报警信号的。因此,不能用火灾显示盘代替区域火灾报警控制器。


好好干   回复: yizhongdayang2024-01-26 19:36

能不能不设置这个区域报警器,为什么其他好多小区都没设置

0    0 [回复]举报