消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

两套湿式报警阀组压力变化不一致

两个车间各自有一套湿式报警阀,共用一套给水设备,一套系统的系统侧压力随供水侧压力变化,另一套系统的系统侧压力基本保持不变,哪一套系统有问题?(喷淋泵到车间的埋地给水管道有漏点,所以供水侧压力会有变化)

消防网友80293 | 2023-11-24 10:27
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

阳明心 2023-11-24 12:05 00 [回复]举报

可能7#报警阀的压力平衡小孔被堵塞了

我的是昵称 2023-11-24 13:24 10 [回复]举报

3号有问题,估计是报警阀阀瓣没关闭,系统侧会随着供水侧的压力降低而降低。正常情况下,喷头爆掉洒水了,系统侧的压力降低,,供水侧比系统侧压力大,阀瓣打开水进入到报警管路压力开关动作起泵水力警铃响。排除掉系统侧大量漏水或喷头爆了之外,系统侧的压力不应有波动。你看看报警管路的常开阀门是不是关了,如果关了,打开后报警管路有动作就是报警阀故障。

消防网友80293   回复: 我的是昵称2023-11-24 19:23

你是懂行的,应该是阀瓣关不严,这个报警阀还是新的,刚装的

0    0 [回复]举报

阿龙   回复: 消防网友802932023-12-18 08:27

你这个可能阀瓣里面有渣子小石子卡主了,你可以把报警阀上腔阀门先关死,打开泄水阀冲洗一下,然后关闭下腔阀门,等水排空了关闭泄水阀。最后先打开上腔阀门把阀瓣先压住,最后再打开下腔阀门。这个方法可能会帮到你

1    0 [回复]举报

关闭

关闭

手机APP下载