消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

有多个无开可开启的外窗的小于50m2的房间,这些无窗房间总面积大于200m2,但是走道长度没有超过20米,是否需要设计机械排烟,如何设置?

有多个无开可开启的外窗的小于50m2的房间,这些无窗房间总面积大于200m2,但是走道长度没有超过20米,是否需要设计机械排烟,如何设置?

赖峰 | 2023-11-09 10:21
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

阳明心 2023-11-09 10:53 00 [回复]举报

8.5.4 地下或半地下建筑(室)、地上建筑内的无窗房间,当总建筑面积大于200m²或一个房间建筑面积大于50m²,且经常有人停留或可燃物较多时,应设置排烟设施。


看看是否经常有人停留,或可燃物是否较多。

戊二烯   回复: 阳明心2023-11-09 14:46

帮忙把结论补完整。如果符合本条,即便走道长度不超过20米,也要设置机械排烟。

1    0 [回复]举报

阳明心   回复: 戊二烯2023-11-09 15:38

谢谢补充

0    0 [回复]举报

潘天坤 2024-06-19 22:27 00 [回复]举报

建筑防火通用规范实施指南有提到:在建筑中存在无窗房间的区域,当每间房间的建筑面积小于或等于50平方米, 这些房间的总建筑面积大于200平方米时(这条规定的总建筑面积不包括房间外的疏散走道等公共区域的面积),在房间内可以不设置排烟设施,但应在房间外的公共区设置排烟设施。

根据楼主的描述,有几种方案:

1、每间房间均设置满足要求的机械排烟口

2、房间不设置排烟设施,在房间外的公共走道设置满足要求的排烟设施

关闭

关闭

手机APP下载