消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

配电室窗户

厂房配电室与相邻控制室之间隔墙上使用可开启铝合金门窗,是否符合规范要求?

轻羽 | 2022-12-10 11:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

张牙舞爪的张 2022-12-10 11:47 00 [回复]举报

不符合。设备间防火分隔要求是2h隔墙➕1.5h楼板与甲级防火门进行分隔。

轻羽   回复: 张牙舞爪的张2022-12-10 22:44

如果门是防火门,窗户是可开启铝合金窗,是否符合规范?

0    0 [回复]举报

张牙舞爪的张   回复: 轻羽2022-12-11 10:44

不可以开窗啊。配电间等设备用房必须采用无门窗洞口的防火隔墙。

0    0 [回复]举报

轻羽   回复: 张牙舞爪的张2022-12-15 06:19

在建筑设计防火规范3.3.8条文说明里,乙类厂房配电站设观察窗时,允许采用不燃材料制作并且不能开启窗。如果丙或丁厂房是否可以设铝合金可开启观察窗?

0    0 [回复]举报

张牙舞爪的张   回复: 轻羽2022-12-15 18:23

第一:乙类厂房配电室能开窗的前提,低于10kw且属于乙类厂房专用配电室,能设不可开启乙级防火窗。

第二:他问的是配电室与控制室之间开窗是否符合要求。开窗就不符合设备用房之间的防火分隔。配电室与厂房之间跟设备房与设备房之间分隔不一样。

1    0 [回复]举报

老骥伏枥 2023-01-30 17:44 00 [回复]举报

乙类厂房配电室,采用不可开启的甲级防火窗。

关闭

关闭

手机APP下载