消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防设施-供配电

单位是三级负荷供电。请问消防泵房最末一级配电柜必须双电源吗?

川人 | 2022-09-05 14:26
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

南明离火 2022-09-05 15:38 00 [回复]举报

弄个双回路

倜圳 2022-09-05 16:32 00 [回复]举报

按GB50016-2014第10.1条确定消防用电负荷等级;再按GB51348-2019第3.2.8~12条确定电源和回路数。

huanglong3721 2022-09-06 16:08 00 [回复]举报

消防泵可采用柴油泵


坚持 2022-09-09 11:29 10 [回复]举报

石峥嵘:当某建筑物的消防用电为三级负荷,且只有一台终端变压器时,双回路供电的意义不大,应可以施行单回路供电。

同时,考虑《建规》10.1.8有明确要求,对于有些要求三级负荷也采用双回路供电的观点,应予尊重。

根据《建筑设计防火规范》10.1.8要求:消防控制室、消防水泵房、防烟和排烟风机房的消防用电设备及消防电梯等的供电,应在其配电线路的最末一级配电箱处设置自动切换装置。也就是说,这些设备均需要采用双回路供电的方式,在现场设置双回路切换装置。

疑问当某建筑物的消防用电为三级负荷时,以上情形是否需要双回路供电?

解答根据规范要求:一级负荷应由双重电源供电,二级负荷要尽可能采用两回线路供电。因此,在一级负荷和二级负荷中,消防用电设备均具备双电源供电的条件,可以实现双回路供电。但是,三级负荷没有双电源或两回线路供电的要求,双回路供电的意义存疑。

综上,当某建筑物的消防用电为三级负荷时,双回路供电的意义不大,应可以施行单回路供电,不需要在配电线路的最末一级配电箱处设置自动切换装置。

注1:三级负荷中,在设置有两台终端变压器的情况下,从变压器至消防设备已具备设置双回路供电的条件,应采用双回路供电。

注2:考虑《建规》10.1.8有明确要求,对于有些要求三级负荷也采用双回路供电的观点,应予尊重。


关闭

关闭

手机APP下载