消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

中间仓库和车间的防火墙耐火极限的要求是3小时还是4小时。

3.2.9 甲、乙类厂房和甲、乙、丙类仓库内的防火墙,其耐火极限不应低于4.00h。

3.3.6 厂房内设置中间仓库时,应符合下列规定:
    1 甲、乙类中间仓库应靠外墙布置,其储量不宜超过1昼夜的需要量;
    甲、乙、丙类中间仓库应采用防火墙和耐火极限不低于1.50h的不燃性楼板与其他部位分隔;
    3 丁、戊类中间仓库应采用耐火极限不低于2.00h的防火隔墙和1.00h的楼板与其他部位分隔;
    4 仓库的耐火等级和面积应符合本规范第3.3.2条和第3.3.3条的规定。


这两条结合起来看是不是表示 中间仓库和车间的防火墙也需要4个小时的耐火极限?

消防网友48598 | 2022-07-07 16:09
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

陈曲 2022-07-07 16:26 00 [回复]举报

甲、乙类厂房和甲、乙、丙类仓库“内”的防火墙,其耐火极限不应低于4.00h

内是重点

消防网友48598   回复: 陈曲2022-07-07 16:38

我原来也是这样理解的,在这里搜索中间仓库的一个探讨,里面明确写的是4h的防火墙。个人理解觉得3小时就可以了。不知道规范组编写的时候这个内是不是表面上理解的意思,是用于仓库与仓库之间的防火分区。而不是车间和仓库的防火分隔。

0    0 [回复]举报

陈曲   回复: 消防网友485982022-07-07 16:45

就是字面意思 甲、乙类厂房和甲、乙、丙类仓库里面的防火墙就得4小时

0    0 [回复]举报

消防网友48598   回复: 陈曲2022-07-07 16:50

0    0 [回复]举报

消防黄河 2022-07-07 18:40 00 [回复]举报

甲乙丙类仓库包括中间仓库4小时。

关闭

关闭

手机APP下载