天然气加压站里的自备应急柴油发电机组能否更换为天然气发电机组?

如题,如果采用天然气供气形式发电,防火措施有何要求?请专家帮忙解答。

| 2022-05-12 16:17
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

石小东 2022-05-17 12:35 10 [回复]举报

你这个在做安全评价时有可能无法通过审核。柴油应急发电机组配有柴油罐,可充分保证外电切断状态下的应急发电;如果使用天然气作为应急发电机组燃料,无法保证天然气源切断情况下,应急供电正常。如果你储备液化天然气罐,安全管理成本要高于储备柴油,从火灾危险性来看,大部分柴油属于丙类液体,而天然气属于甲类气体。