消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

室内消火栓的保护距离

我们是丙类生产厂房,建筑物内有很多房间,咨询一下室内消火栓水带20米,充实水柱10米,保护半径30米,这个30米是在平面上画个半径的圆的直线距离吗?还是需要考虑墙体和设备的阻挡而引起的距离长度吗?

法国红酒 | 2021-10-30 10:52
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

刘丽波 2021-10-31 07:14 00 [回复]举报

规范中要求的是需要两股水柱时布置间距不超过30米。单个消火栓的保护半径根据消水规10.2.1计算所得,本工程应为26-28米,按保护半径校核时需考虑墙体等遮挡,不影响走水带的设备可以不与考虑。

乐清迦累得 2021-10-31 20:02 00 [回复]举报

你这个水带长度不满足30米的要求,正常水带25米时,满足折减系数0.8-09后,加上sin45*10m的=27.07-29.57米的;         厂房的规范是直线距离,看图是直线距离,  民用规范是直线距离,看图是步行距离,考试时按步行距离, 如果是现实验收,是要考虑墙体和设备等障碍物的,  具体看平面布置图是否满足要求了

关闭

关闭

手机APP下载