稳压泵停泵、启泵压力与消火栓设计工作压力的关系?

稳压泵停泵、启泵压力与消火栓设计工作压力的关系?

漂移 | 2021-09-03 13:15
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

工程新一 2021-09-03 14:19 20 [回复]举报

消火栓工作压力P1,因设有稳压泵,需满足最不利点不低于0.15MPa,低压这个压力时,干管压力开关连锁启泵;

稳压泵启泵压力P2,大于P1,大于值0.07MPa~0.10MPa,防止稳压泵未启动先启动消火栓泵;

稳压泵停泵压力P3,大于P2,满足稳压泵启泵次数小于15次/小时,受漏水量与稳压罐容积影响;

所有压力均查看同一点位,其他点位压力根据高差换算