低压配电室可否使用二氧化碳灭火器?

GB50140-2005《建筑灭火器配置设计规范》4.2.5条的条文解释中的表格标识:“对于E类火灾,二氧化碳灭火器适用于带电的B类火灾。”低压配电室火灾是否应该属于E类火灾中带电的A类火灾范畴?这样的话,按条文解释,二氧化碳灭火器是不适用于600V以下的低压配电室火灾的呀。。

且二氧化碳灭火器不适用于A类火灾,那配电室断电的情况下是A类,也不适用啊。。

且根据DL5027-2015《电力设备典型消防规程》F3.1“二氧化碳灭火器适用于扑灭600V 以下的带电B类火灾。”

另外,带电的B类火灾都有什么?能举个例子么??

迷茫了,还请各位大神给予解答,谢谢!!

DAMING | 2025-01-03 10:36
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

喧哗 2025-01-03 12:05 00 [回复]举报

个人认为,只有E类火灾场所中,存在油类的变压器、发电机房才可以按B类级别选二氧化碳灭火器,普通配电室均按A类

DAMING   回复: 喧哗2025-01-06 08:35

嗯嗯!!油类变压器场所电压都高于600V,那这样的话,只有汽柴油发电机房才能选配二氧化碳灭火器了~~然后考虑到还有其他介质,还得考虑另配一个其他灭火器~~感觉二氧化碳这个灭火器好鸡肋,哈哈~~

0    0 [回复]举报

溜达呀 2025-01-03 17:15 10 [回复]举报

低压配电室可以使用二氧化碳灭火器。

根据《建筑消防设施通用规范GB55036-2022》 E类火灾场所应选择适用于E类火灾的灭火器。带电设备电压超过1kV且灭火时不能断电的场所不应使用灭火器带电扑救。

 二氧化碳的钢瓶上很清楚的写着可以灭E类火灾(断电、低压)

DAMING   回复: 溜达呀2025-01-06 08:39

以前我也一直这么认为的~~回看了一下GB50140-2005《建筑灭火器配置设计规范》4.2.5条的条文解释,E类火灾又给分成了带电A类火灾和带电B类火灾~~二氧化碳只适用于带电B类火灾,与DL5027-2015《电力设备典型消防规程》F3.1描述相符~~

0    0 [回复]举报