消防问答 > 防烟排烟 提问

如图所示这样这是排烟系统符合要求吗

这份图纸一层设计了2个防烟分区,被隔离门隔开的走道和上部区域没有设计防烟分区和排烟设施这样设计合理吗?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 5 回答

@mad 24-05-27

走道没超20m长度,上部房间目测面积小于50m2而且有外窗,可以不考虑排烟


1 0 [回复]举报

南明离火 24-05-28

就看走道长度有没有超

0 0 [回复]举报

潘天坤 24-06-03

1、需要明确两个走道总长度是多少,是否满足疏散走道排烟系统设置条件(从图纸来看,属于医院办公室等区域,疏散走道20米要求),一般不认可通过设置门分隔来规避疏散走道长度而不设置排烟设施。

2、如果疏散走道总长度超过走道排烟设施的设防要求,那么得考虑走道排烟设施。如果不满足设防要求,则走道不需要考虑排烟情况。

3、需要明确医生办公室、复苏室、洗消室、内窥室等房间的建筑面积及可开启外窗设置情况。

4、需要明确是否引用《医院洁净手术部建筑技术规范》(GB50333-2013),规范内对无窗建筑或建筑物内无窗房间有防排烟系统及补风系统设置要求。

0 0 [回复]举报

玺望成真   回复: 潘天坤24-06-06

如图左侧走道设置了排烟,隔离门间的走道和次走道上面的房间未设置排烟,房间的面积和走道的长度都没达到设置排烟的标准。

0 0 [回复]举报

潘天坤   回复: 玺望成真24-06-07

一般不认可用分隔措施来分隔疏散走道长度以规避排烟系统设置要求,如果可以采取这类措施,多做几个门是不是就不需要设置排烟系统了

0 0 [回复]举报

最新问题

关闭

关闭