请教老师关于二氧化碳灭火种类的问题

老师好:GB/T50193-1993中关于二氧化碳灭火种类的描述“1.0.4 二氧化碳灭火系统可用于扑救下列火灾:    1.0.4.1 灭火前可切断气源的气体火灾。     1.0.4.2 液体火灾或石蜡、沥青等可熔化的固体火灾。      1.0.4.3 固体表面火灾及棉毛、织物、纸张等部分固体深位火灾。      1.0.4.4 电气火灾。”。包括了固体火灾。但GB50140-2005中,“4.2.1 A类火灾场所应选择水型灭火器、磷酸铵盐干粉灭火器、泡沫灭火器或卤代烷灭火器。”中A类火灾没有二氧化碳灭火器,特别是条文说明表三中,二氧化碳明确不适合A类火灾。请教老师两个国标如何理解和应用。

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

安洪全 23-08-07

两本规范应用场景不同,一本是二氧化碳灭火系统(自动灭火系统里的气体灭火系统),一本是灭火器。

灭火器从的灭火剂的用量与浸渍时间上都没法和二氧化碳灭火系统用法不同,所以两个要求不冲突,是同一种灭火剂在不同领域应用下的不同要求。


二氧化碳灭火系统设计规范(2010版) GB/T50193-1993


建筑灭火器配置设计规范 GB50140-2005

0 0 [回复]举报

消防网友30777   回复: 安洪全23-08-08

谢谢您的指导。可不可以理解为:二氧化碳灭火系统可以配置在计算机机房,但手提式二氧化碳灭火器配置在计算机机房就不符合规范的规定。

0 0 [回复]举报

安洪全   回复: 消防网友3077723-08-08

0 0 [回复]举报