消防问答 > 消防给排水 提问

室内消火栓系统

5层办公楼的室内消火栓管网是否可以直连市政管网

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 1 回答

消防网友78337 23-03-01

如果建筑符合

建筑防火通用规范 GB55037-2022

8.1.7.6 建筑高度大于15m或建筑体积大于10000m³的办公建筑、教学建筑及其他单、多层民用建筑;

要设置室内消火栓。


是否室内消火栓管网是否可以直连市政管网,理论上可以,但是需要市政管网的流量及压力满足设计要求。

最不利点消火栓栓口动压不应小于0.25MPa,且消防水枪充实水柱应按10m计算。


否则需要消防泵,

是否需要消防水池见下:

4.3.1 符合下列规定之一时,应设置消防水池:     1 当生产、生活用水量达到最大时,市政给水管网或入户引入管不能满足室内、室外消防给水设计流量;     2 当采用一路消防供水或只有一条入户引入管,且室外消火栓设计流量大于20L/s或建筑高度大于50m时;     3 市政消防给水设计流量小于建筑室内外消防给水设计流量。

见6.1.9,需要设置高位消防水箱。


问题逻辑是,直连市政管网,是否必须消防泵,消防水池,高位消防水箱。

有消防水池必有消防泵。

简单说,只有市政管网保持常高压,且水量满足,才能直接市政。



0 0 [回复]举报

最新问题

关闭

关闭