单层建筑的商店10000平米的疏散宽度

一万平米的单层超市购物,人员密度0.43,疏散宽度0.75。疏散总宽度310米,这得怎么实现?或者安全出口算大多几个

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 5 回答

22-09-26

二级耐火等级百人宽取0.65,疏散总宽度为27.95米;

三级耐火等级百人宽取0.75,疏散总宽度为32.25米,不是310米。

4 0 [回复]举报

aalwbw 22-11-08

楼上说的对,另外每个安全出口的净宽不应小于1.4米,除法计算。

0 0 [回复]举报

张牙舞爪的张 22-11-18

大于等于3000平米取下限,小于3000平米取上限。该商店一万平米,人员密度应该取0.43。根据人员密度算出该层设计人数为4300人,再根据百人疏散宽度取0.65(耐火等级三级取0.75)得出27.95米,且每个出口宽度大于等于1.4米。

0 0 [回复]举报

一对麻辣小龙虾 22-12-28

你算得对吗

0 0 [回复]举报

北洼 23-10-17

10000*0.43*0.75/100=32.25m

0 0 [回复]举报