排烟系统的支管是按风机风量设计还是按防烟分区风量设计的

当一个排烟系统担负多个防烟分区时,净高一样且小于6m时,排烟风机的风量一定会比其中一个防烟分区的风量大。那么火灾时仅打开着火防烟分区,这个防烟分区的风管风口如果按本身风量设计,它的风管和风口的风速很可能会超的。所以排烟系统的支管是按风机风量设计还是按防烟分区风量设计的?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

刘丽波 22-03-11

支风管按防烟分区风量确定。

1 0 [回复]举报

最帅游客 22-03-11

系统的排烟量要么是最大的防烟分区,要么是相邻之和最大的。所以支管应是按分区。

0 0 [回复]举报

苏莱曼 22-03-11

规范上有列子的,自己看看就知道了。

0 0 [回复]举报

牛疼 22-03-13

支风管按防烟分区风量确定。

现在的防排烟系统一般都会安装风压控制调节设备,不用考虑超速的可能。