消防问答 > 建筑防火 提问

乙类厂房防火间距问题

请问防火规范图集3.4.1的图示1没有标明的乙类厂房的防火间距应该怎么卡?不能贴近3.3.5规定的以外的那就是没有其他防火间距不限的情况?那为什么实施指南第81页的示意图上画着乙类?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 1 回答

牛丫头消防课堂 25-06-17

我个人理解,乙类厂房防火间距调整时和甲类厂房同等对待,因为考虑它的爆炸性对周围建筑的影响。你再看看建规3.4.1表注2,最后一句话:甲、乙类厂房(仓库)不应与本规范第3.3.5条规定外的其他建筑贴邻。

0 0 [回复]举报

最新问题

关闭

关闭