消防问答 > 安全疏散 提问

楼梯间转角平台应急照明灯

消防平面图中,楼梯间平面图吸顶应急照明灯只有1~2具,现场一层至二层实际转角平台有4个。

现场安装是每个转角平台都安装,还是按照平面图安装。

有没有消防规范涉及到这个条件。

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 2 回答

牛丫头消防课堂 25-06-05

主张按图施工,因为正常情况下,设计人员需要经过照度计算的,即使以后测试达不到规范要求,只要你按图施工,那么施工人员没有责任。如果自己改变安装位置、安装高度,如果实测照度不满足规范要求,施工人员就有责任。

0 0 [回复]举报

李勤 25-06-09

图纸经过图审,应按图施工。对于应急照明照度情况涉及到选用灯具的类型、设置高度、设置间距及安装方式。图纸设计时照度都经过计算进行的平面布局。

1.建议不要改变原有灯具设计位置

2.如在原有位置基础上,施工单位自行增设,严于规范可以。但涉及到你最后结算时业主对这些工程量是否认可的问题。

0 0 [回复]举报

最新问题

关闭

关闭