消防问答 > 自喷灭火系统 提问

试水阀与末端试水装置区别只是位置不同吗?

每个报警阀组控制的最不利点洒水喷头处应设末端试水装置

每个楼层及防火分区都要有试水阀,而每个报警阀组控制的最不利点洒水喷头处应设末端试水装置。

每个楼层及防火分区的试水阀组件里面包括压力表吗?如果包括了 那它的组件跟末端试水装置一样了,就只是安装位置不同而已了,

如果不包括该楼层压力是不是就不能实时监控了呢?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 11 回答

喧哗 25-01-23

试水阀不用压力表,试水阀这个楼层压力不用监控,只看末端试水装置的压力表就行了,末端试水装置就是压力最低点。

0 0 [回复]举报

徐海金 25-01-23

不一样,末端试水多了个末端试水装置,一般装一个同楼层或防火分区内的最小流量系数洒水喷头;试水阀不需要安装这喷头,直接DN25管就行。其他一样

0 0 [回复]举报

LHH2737 25-01-23

试水阀没有压力表

实际上业主和物业都怕管子爆开,没事都不敢启泵,所以基本不存在压力过大的问题,只会存在压力过小的问题,这个时候只要在最不利点安装压力表就行,最不利点都没问题,下面那些只安装了试水阀的压力也不会有问题

0 0 [回复]举报

小唐12321 25-01-23

差不多,少一个压力表,但是很多现场试水阀也安装压力表

0 0 [回复]举报

消防搬砖师 25-01-23

1.设置位置不同:末端试水装置设置在报警阀组最末端,试水阀设置在每个防火分区和每个楼层

2.设备不同:末端试水装置是由压力表、试水阀、试水接头组成

3.作用不同:末端试水装置是为了检测系统功能和性能,试水阀为了测试设备和管道。

0 0 [回复]举报

潘天坤 25-01-23

规范描述的很清楚,楼主也复述了

试水阀不需要压力表,当然多做也不算错,但是规范没有要求必须设置压力表

0 0 [回复]举报

本安消熊   回复: 潘天坤25-01-24

统一回复谢谢潘天坤、消防搬砖师、小唐12321、LHH2737、徐海金、喧哗等专家的耐心解惑,大家理解都差不多,只是现实遇到好多设计图纸楼层试水阀都配压力表了,要说是少数设计人员解读规范误差吧,但是目前遇到的大多数都这样设计了,虽然一个压力表也没有多少钱,但是从优化经济成本角度考虑感觉有点冗余了。

0 0 [回复]举报

潘天坤   回复: 本安消熊25-01-24

设计可能会多提高要求,也不能说是设计错误,这个情况如果不想安装可以找设计单位沟通设计变更取消。不过有安装应该也有费用呢,按图施工也可以结算的

0 0 [回复]举报

本安消熊   回复: 潘天坤25-02-10

好的,多谢耐心解惑!

0 0 [回复]举报

云中飞翔 25-01-24

每个报警阀组最不利点晒水喷头处设置末端试水装置,该报警阀组控制的其他楼层和防火分区设置DN25的试水阀。末端试水装置设置有试水阀、压力表和试水接头,而报警阀控制的其他楼层和防火分区仅设置试水阀。

0 0 [回复]举报

本安消熊   回复: 云中飞翔25-02-10

多谢回答!

0 0 [回复]举报

最新问题

关闭

关闭